I made a run of 3/4 emt that I 90'd off the ceiling, down 17inches, then had to offset to the wall to finish the run. the total length of the unsupported emt was 6' 7". The inspector said this was no good as the conduit out in the air like that needed to be supported closer together than 6' 7" according to the NEC. the local AHJ sticks to the NEC on conduit. I can't find it. could some one help? as far as I can see emt needs to be supported every 10' according to 358.30 A and/or B