T tim89s Member Location Brush Prairie WA Mar 18, 2004 #1 Is there any type of code violation going from EMT to PVC? The installation will be outdoors. I will use a rain tight EMT Connector to a Ridgid Coupling then to a PVC male adapter.
Is there any type of code violation going from EMT to PVC? The installation will be outdoors. I will use a rain tight EMT Connector to a Ridgid Coupling then to a PVC male adapter.
tshea Senior Member Location Wisconsin Mar 18, 2004 #2 Re: EMT to PVC Why not use a female pvc fitting? Remeber to pull a ground wire!
ryan_618 Senior Member Location Salt Lake City, Utah Mar 18, 2004 #4 Re: EMT to PVC No problem at all. God bless rigid couplings!!! As mentioned before, make sure you pull an EGC.
Re: EMT to PVC No problem at all. God bless rigid couplings!!! As mentioned before, make sure you pull an EGC.