Hello forum members, this is my first post on this forum. I've been reading it for a couple of years now, and I think it is fantastic. My question is concerning the use of 3/4 " EMT as the Equipment Grounding Conductor on a lighting branch circuit. I have a contractor on one of my jobs who argues that because of Article 250.118 (4), and 250.134 (A), he can use the conduit as his EGC, and doesn't have to pigtail his junction boxes (in which the CCCs have joints made up) to the ground wire within the conduit. I say that he does have to pigtail the grounds in the boxes because of 314.4. Also, the handbook states, in 250.134, " To keep the impedance at a minimum, it is necessary to run the equipment grounding conductor IN the same raceway or cable as the circuit conductor(s)." I also know that if a junction box is not pigtailed, if the conduit comes apart between the box and the panel, the box is no longer grounded, and could become energized if a short occurs.
Is there something in Article 250 that I am overlooking? Any answers would be greatly appreciated.
Is there something in Article 250 that I am overlooking? Any answers would be greatly appreciated.