In an industrial factory, is it permissible to run EMT on the ceiling? Spikes and screws protrude from work done to the roof and from items attached to the roof. I am thinking EMT is not permitted in this situation, is this correct?
 
In an industrial factory, is it permissible to run EMT on the ceiling? Spikes and screws protrude from work done to the roof and from items attached to the roof. I am thinking EMT is not permitted in this situation, is this correct?

Is it the bottom side of the roof, or is it a ceiling?
 
Pipe running under roofs

Pipe running under roofs

In an industrial factory, is it permissible to run EMT on the ceiling? Spikes and screws protrude from work done to the roof and from items attached to the roof. I am thinking EMT is not permitted in this situation, is this correct?

Article 300.4(B)(2)(E) A cable, raceway, or box installed in exposed or concealed locations under metal-corrugated sheet roof decking shall be installed and supported so there is not less than 38 mm(1 1/2 in) measured from the lowest surface of the roof decking to the top of the cable, raceway, or box.
As long as you're not in a hazardous area, you should be OK.
 
Article 300.4(B)(2)(E) A cable, raceway, or box installed in exposed or concealed locations under metal-corrugated sheet roof decking shall be installed and supported so there is not less than 38 mm(1 1/2 in) measured from the lowest surface of the roof decking to the top of the cable, raceway, or box.
As long as you're not in a hazardous area, you should be OK.

Pretty sure that is just 300.4(E).
 
Thanks everyone, I found art. 300.4 (E) after I posted my first thread. New to this forum thing. Please bear with my ignorance at this point.
That section has not been around all that long - maybe first added in 2008 or 2011? Is possible you may have older install that has EMT run in the now restricted area.
 