R rich000 Senior Member May 31, 2011 #1 Is this installation in violation of 358.30(A)? i.e. It is not securley fastened within 3 feet of the cabinet? Thank you. Attachments IMG_1196.jpg 139.1 KB · Views: 0 Last edited: May 31, 2011
iwire Moderator Staff member Location Massachusetts May 31, 2011 #2 IMO yes, it also looks more than 5' so the exception cannot be used.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) May 31, 2011 #3 Yes, and it's quite common on those exact types of installations, 90? bends into the top of the equipment.
raider1 Senior Member Staff member Location Logan, Utah May 31, 2011 #4 I agree with Bob and Rob, a violation. Chris
J jusme123 Senior Member Location NY Occupation JW May 31, 2011 #5 ...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!!
R rich000 Senior Member Jun 7, 2011 #6 jusme123 said: ...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!! Click to expand... The switchgear would have to rated for support. Correct?
S sameguy Senior Member Location New York Occupation Master Elec./JW retired Jun 7, 2011 #8 Drop rod from above and add strut