EMT vertical support

Status
Not open for further replies.

rich000

Senior Member
Is this installation in violation of 358.30(A)? i.e. It is not securley fastened within 3 feet of the cabinet? Thank you.
 

Attachments

  • IMG_1196.jpg
    IMG_1196.jpg
    139.1 KB · Views: 0
Last edited:
Yes, and it's quite common on those exact types of installations, 90? bends into the top of the equipment.
 
...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!!
 