R rich000 Senior Member May 31, 2011 #1 Is this installation in violation of 358.30(A)? i.e. It is not securley fastened within 3 feet of the cabinet? Thank you. Attachments IMG_1196.jpg 139.1 KB · Views: 0 Last edited: May 31, 2011
Is this installation in violation of 358.30(A)? i.e. It is not securley fastened within 3 feet of the cabinet? Thank you.
iwire Moderator Staff member Location Massachusetts May 31, 2011 #2 IMO yes, it also looks more than 5' so the exception cannot be used.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 31, 2011 #3 Yes, and it's quite common on those exact types of installations, 90? bends into the top of the equipment.
Yes, and it's quite common on those exact types of installations, 90? bends into the top of the equipment.
raider1 Senior Member Staff member Location Logan, Utah May 31, 2011 #4 I agree with Bob and Rob, a violation. Chris
J jusme123 Senior Member Location NY Occupation JW May 31, 2011 #5 ...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!!
...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!!
R rich000 Senior Member Jun 7, 2011 #6 jusme123 said: ...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!! Click to expand... The switchgear would have to rated for support. Correct?
jusme123 said: ...use kindolf L brackets and build a support off the top of the switchgear (bolt L brackets to the top of the gear), and your to code!! Click to expand... The switchgear would have to rated for support. Correct?
S sameguy Senior Member Location New York Occupation Master Elec./JW retired Jun 7, 2011 #8 Drop rod from above and add strut