Electroplaxes
Member
- Location
- Nunica, MI
I'm looking for any code references for and against that could help me. I have an exterior tap service 1000A to 400A/600A/600A. The trough is fed with schedule 80 PVC. Then it is piped from the trough down with EMT and RT connectors to a CT cabinets (top penetration). CTs are then connected with close nipples, locknuts and a myer hubs up into the discos. From the discos back down and out to the distribution panels via Schedule 40 PVC. NEC wise I don't think there is any violations. The reason for this post is some of the older guys in my shop say you can't use EMT for non-fused conductors. They are also stating it is required to have myer hubs in lieu of RT connectors. I think most of this is form a "that's the way we've always done it" view point. So now they're page turning trying to stick it to me. I don't some much care about them as I do the inspector, which is form around the same era as them. I'd like to be prepared if he raises the same questions. And above all if I am in violation I'd like to change it prior to a failed inspection and terminated wire. Thanks ahead of time.