- Simi Valley, CA
I just want to see if everyone is in agreement. Connectors and couplings for EMT installed under a carport (open on all sides, with pitched roof) shall be compression type.
Is the EMT side pitched as well?
John compression tight does not mean wet location or damp location. They make rt connectors and couplings which happen to be compression type but not all compression fittings are WR. IMO, a set screw conn. is fine there if a compression connector is allowed but I am not sure how they are listed.
I'm aware of that, should be the "blue" compression fittings. I was just trying to keep the question short and to the point.John compression tight does not mean wet location or damp location. They make rt connectors and couplings which happen to be compression type but not all compression fittings are WR. IMO, a set screw conn. is fine there if a compression connector is allowed but I am not sure how they are listed.
If you look at 314.15 it says, "in damp or wet locations,........and fittings shall be placed or equipped so as to prevent moisture from entering or accumulating within........or fitting.........and fittings installed in wet locations shall be listed for use in wet locations.
So I know the first j-box is in a wet location (base of column) then it goes up to the underside of the roof and runs along there (damp location). So does it need to be a wet location fitting (blue) or can it be a compression fitting or even a set screw fitting?
No it comes up one of the columns and then runs right below the peak to feed some lights.
Very ugly job. One run has eight 90's in it and everything is put together with set screw connectors.
I'm not sure that for connectors there's a difference between "wet" and "damp", but I'm not staring at the white book right now.
Our inventory program has EMT set screw connectors as $0.59, compression at $1.01, and rain tight at $2.58, all for 1/2". If the carport is open on all sides, there's a good chance every fitting will, at one time or another, be subject to wind driven rain. My opinion, and worth every cent you're paying for it, is let the customer pay for the rain tights. One less potential call back to worry about. One less inspector to give you a hard time about it, come to think of it.
I see no need for anything other than set screw connectors and couplings for EMT run on the underside of the roof.