Enclosure Cover Requirement

Status
Not open for further replies.

mgoslak

Member
Does anyone know of a code requirement for enclsoure covers? For example, I'm looking for a code that would specifically tell you whether it is acceptable or not to install a 3' x 3' JB 30' off the ground w/ only a slotted head screw on type cover (versus, a hinged cover). The concern is that the cover falls off an injures the worker.
 
Re: Enclosure Cover Requirement

I believe the code only requires that covers for boxes and enclosures be compatible with the box and that they are suitable for the conditions of use. See section 314.28(C).
 
Re: Enclosure Cover Requirement

Originally posted by mgoslak:
Does anyone know of a code requirement for enclsoure covers? For example, I'm looking for a code that would specifically tell you whether it is acceptable or not to install a 3' x 3' JB 30' off the ground w/ only a slotted head screw on type cover (versus, a hinged cover). The concern is that the cover falls off an injures the worker.
regardless of what the code says, do you really want to save $20 or so using this type of enclosure that far off the ground? I have to beleive the aggravation factor is worth the cost differential.
 
Status
Not open for further replies.
Top