The OP said it was a gutter. It's not a wireway unless it is listed as a wireway.I think that the term gutter is incorrectly used in the OP and it's actually a wireway.
The OP said it was a gutter. It's not a wireway unless it is listed as a wireway.I think that the term gutter is incorrectly used in the OP and it's actually a wireway.
Gutters as covered by Article 366 are very rare. Most everything that is called a gutter in the field is a wireway covered by Article 376.The OP said it was a gutter. It's not a wireway unless it is listed as a wireway.
Yup, that was my point. The term gutter is quite often misused when the raceway is actually a wireway.Gutters as covered by Article 366 are very rare. Most everything that is called a gutter in the field is a wireway covered by Article 376.
If the item in connected to the equipment via raceways it is an Article 376 Wireway, and not an Article 366 Auxiliary Gutter.
It's like saying 'conduit' when you're talking about EMT. We can reasonably assume the OP was referring to a wireway.Yup, that was my point. The term gutter is quite often misused when the raceway is actually a wireway.