ENERGIZED WORK ?

Status
Not open for further replies.

jimbo123

Senior Member
If I follow 70e as a electrical safety plan and someone is interacting with mcc 's that have not been maintained as in pm should those workers have a energized work permit to do this work ? I believe this is a requirement . Would like to here other opinuins.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Energized work deals mainly (or entirely) with exposure to voltages through accidental contact.
If there is no voltage exposure (not opening enclosure, etc.) then I would not see that an energized work permit would apply.

However the arc flash risk (but not magnitude!), even with the doors closed, would be greater than if the devices had been properly maintained. Given that, a higher level of PPE may be justified. If the likely energy level goes beyond 40, then the interaction simply cannot be done with the devices energized, hot work permit or not.
 