Hey all I was asked to go thru a industrial building thats been vacant to clean up a mess and get some power on for lights as its going on the market.
It has only been empty a few years but druggies and thieves have broke in and stolen lots of copper
There are burn marks in a gutter and a few disconnects where something very bad happened, so thats probably when the copper thieves left.
The utility has cut the power at the primary on the pole, but they will turn it on when I say its OK to.
The service is mostly OK no burn marks though they did possibly get in the MDP,
or the former tenant may have removed feeders.
Service is about 10 years old I'd hate to replace it as the building is for sale.
Someone removed feeder breakers out of the MDP, leaving those 'fingers' that go up to the breakers.
There are empty conduits, conduits just cut off with wire in them its a mess.
I can clean all that up,
I'll remove and save the fingers from the MDP,
put in K/O seals;
fix the gounding / bonding;
Ohm out the service;
I'll make sure nothing else gets energized other than a few lights.
My question for you guys here on the safety forum is should I do any tests before having the utility energize the transformer energizing the main 800A breaker like a megger test?
put in K/O seals;