Jeff1971 said:
... Does the NEC have a demand factor that can be used in the calculation (similar to RV parks, clothes dryers, electric stoves, etc.) to decrease the 374 amps to a lower value?
Living in an area where block heaters are a necessity: I hope not.
I would not consider this a code issue - it's a design issue. Consider this: Is the area one where block heaters are necessary? Does the customer wish to be able to fill the parking lot with vehicles and have them all plugged in and heated all the time? If the answers are, Yes, Yes, Yes - the application is 100%.
Here are some methods to reduce the power required.
1. Redude the number of spaces with receptacles. Consult with the owner, maybe some of the spaces can be unheated
2. Cycle the heater power using a timer, thermostat, and contactors feeding the panels. Consider:
above +20F off
+20 to -30F 50% duty cycle 30min on, 30min off
colder than -30F ON
Use two or four panels so you can drop the max current draw. If the area gets colder than -30F is won't help.
3. Put the transformers out in the parking lot, next to the panels. That will cut down on the fat runs.
carl