Engineer Wants (3) 208V 20A Hand Dryers on 30A Circuit

Status
Not open for further replies.
6.2 amps is for 277 volts. At 208 volts it's rated at 5.6 amps. Resistive load, lower voltage means lower current since current and voltage are directly proportional.

I took the information off of the Xlerator product page.

Silly me. I always thought that higher voltages meant lower amperage. You know... like transmission lines use 7200v and up so the amperage is much lower.

I guess I should rewire my house for 5 volts so I can use tinsel wire.
 
Silly me. I always thought that higher voltages meant lower amperage. You know... like transmission lines use 7200v and up so the amperage is much lower.
That's true when the equipment is built to natch the voltage. When talking about delivering a given power, the P = E x I math applies. To deliver a given power, current varies inversely with voltage. Also, loads like motors use less current when the voltage increases (within its design voltage range).

When talking about applying a different voltage to equipment with no change to the equipment, then the I = E / R Ohm's Law math applies. The current varies proportionately with applied voltage. This describes most electrical loads which behave as resistive loads do. If the voltage increases, so does the current.

I guess I should rewire my house for 5 volts so I can use tinsel wire.
If you apply only 5v to loads designed for 120v, so little current would result that you probably could. 120 / 5= 24, so 1/24 as much current would flow at 5v compared to 120v.

On the other hand, if you want the same amount of power on 5v as you would on 120v, you'd have to be able to supply 24 times as much current, so you'd need very heavy wire.


Look at your car wiring. Battery and spark-plug cables are about the same diameter, but battery cables are mostly conductor, while spark-plug cables are mostly insulation.

Electricity is transmitted at high voltages over distances because insulation is cheaper than conductor, and more importantly, voltage drop is dependent on current, not voltage.


By the way, 7200v is relatively low for even primary distribution. Transmission voltages are in the 100Kv and up range; some long-distance lines are into the megavolt range.
 
Silly me. I always thought that higher voltages meant lower amperage. You know... like transmission lines use 7200v and up so the amperage is much lower.

I guess I should rewire my house for 5 volts so I can use tinsel wire.
little wire in, big wires out

me myself, i like the op profile picture!
 
Where did it come from though? OP never gave any model number that I was aware of.
6.2 amps is for 277 volts. At 208 volts it's rated at 5.6 amps. Resistive load, lower voltage means lower current since current and voltage are directly proportional.

I took the information off of the Xlerator product page.


Other than different voltages looks like they basically only have one model to choose from, wattage of the different volt units are about same anyway.

I have not installed all that many hand dryers so don't know what is common.
 
Silly me. I always thought that higher voltages meant lower amperage. You know... like transmission lines use 7200v and up so the amperage is much lower.

I guess I should rewire my house for 5 volts so I can use tinsel wire.
If a different unit with different resistance to get same output watts then higher volts will be less current.

If same unit has lower voltage applied but resistance remains constant, then current drops, but so does wattage.
 
I would like t know what the MFG recommends for branch circuit protection. It may not be allowed on a 30. I would think this would be a non continuous load so I don't see why you couldn't put 3 on a 20A
 
I would like t know what the MFG recommends for branch circuit protection. It may not be allowed on a 30. I would think this would be a non continuous load so I don't see why you couldn't put 3 on a 20A

I agree, protecting a 5.6 amp appliance at 30 amps could be problematic unless specifically allowed by the manufacturer. Does the NEC permit a 5.6 amp appliance on a 20 amp circuit? If so install all three on a 20 amp circuit and you're code compliant unless the manufacturer or the NEC limits the appliance to a 15 amp circuit or requires an individual branch circuit for each unit.
 
I agree, protecting a 5.6 amp appliance at 30 amps could be problematic unless specifically allowed by the manufacturer. Does the NEC permit a 5.6 amp appliance on a 20 amp circuit? If so install all three on a 20 amp circuit and you're code compliant unless the manufacturer or the NEC limits the appliance to a 15 amp circuit or requires an individual branch circuit for each unit.
I looked on there web site only because there made in my Town (East Longmeadow, Ma). They give voltage, amps, wattage with and without motor for different voltages no other info on branch circ. etc
 
I would like t know what the MFG recommends for branch circuit protection. It may not be allowed on a 30. I would think this would be a non continuous load so I don't see why you couldn't put 3 on a 20A
The rule is 422.11.

A. says if protective device is marked on the appliance then that is what it will be.

B and C don't apply to this particular appliance

D possibly could apply - and has a max of 50 amps (edit) read it again, should not apply because this has no surface heating elements

E - depends if you call this a motor operated appliance - it has a blower motor but the major load is the heating element. If E does apply then max overcurrent is 20 amps for a 13.3 amp or less rated appliance or 150% for all others.

F doesn't apply and G involves motor overload protection for motor operated appliances.
 