I just received an engineers drawing for a 400 amp underground service to a single family house.  Here is what I do not agree with and I am sure I will have support on this forum.  From pad mount transformer he has 6 300mcm xhhw Al being run in single 4" PVC to meter pedestal along with a 1/0 CU ground.  Is the ground wire from padmount to meter pedestal o.k.?  From meter pedestal we have two runs of 4/0 AL xhhw in separate 2 1/2" pvc conduits going to house and each run has a #2 Cu ground wire in it.  First run hits a main disco. inside house for supply of a 200 amp panel at other end of house (PP2) second run hits 200 amp panel (PP1).  Grounding - this is where the problem with design seems to be, is as follows-  #2 CU from water line hitting main disconnect and then 200 amp main panel.  My question here is no detail is given.  Shouldn't  #2 CU be continuous through the main disconnect hitting ground bar and then go on to PP1.  Also is the #2 CU in both runs from meter pedestal correct?  I must admit I am confused with what I have been presented here.  Also am I correct to be keeping my grounds and neutrals seperated with my OCPD being at meter pedestal?? Finally he has me supplying PP2 with 3 4/0 XHHW AL from disconnect and a #8 CU ground.  Now I know this is not right, should be a #4.  I just wanted some input before I respond to engineer with list of issues.  How would you tactfully suggest this appropriately to the engineer?
	
		
			
		
		
	
				
			 
				
 
 
		