Not according to the below. I would also suspect that as long as the feed to the 3 KVA transformer is properly protected it would be O.K. but I will have to keep looking for that issue.
2002 NEC 210.63 Heating, Air-Conditioning, and Refrigeration
Equipment Outlet. A 125-volt, single-phase, 15- or 20-
ampere-rated receptacle outlet shall be installed at an accessible
location for the servicing of heating, airconditioning,
and refrigeration equipment. The receptacle
shall be located on the same level and within 7.5 m (25 ft)
of the heating, air-conditioning, and refrigeration equipment.
The receptacle outlet shall not be connected to the
load side of the equipment disconnecting means.
FPN: See 210.8 for ground-fault circuit-interrupter
requirements.
-Ed