I have this situation and in one of the points in the report I am going to included the statement below, but I have hard time to explaining this to those ignorant a arrogant people. question; is this statement clear? Any help is greatly appreciated
9- At the 102 apartment ?someone? messed the electrical. The multiwire is in one phase using a tandem circuit breaker and this is a no-no, it must be on separated phases protected with a double pole breaker, but also this breaker is damaged because this tandem keep tripping and people resetting again and again. The ?someone? not knowing better, used this multiwire ? black & red ? as a parallel circuit when he joined those conductors at all the receptacles that he replaced and at the same time, for unknown reasons, he lost the neutral and losing the neutral caused on the receptacles that he didn?t ?joined? the ungrounded conductors (black & red) voltages fluctuations and as result, burning out appliances. Also this panel is a Zinsco and I strongly recommended replacing it, it is too old and breakers are not tripping under short circuits. There are several receptacles with no ground attached. New baseboard heaters directly under receptacles outlets, a no-no situation and several other violations. According to the handyman, there are several apartments with the same electrical problems. When your dad shows there and he said that replacing the 15 amps breaker for more ?powerful amps breakers? will solve the problem and he instructed me to so, of course I refused and I lost the job, he demonstrated not only his ignorance but his arrogant way in believing ?I know it all?, disregarding professional and licensed individuals and jeopardizing human lives. This is why I sent the report to Labor & Industries . I hope, for the tenants safety, that you already sent a licensed electrician to deal with that.