I have to agree with some others, if you indeed have 15 KVA and it supplies that many dwellings, it probably is overloaded at times and nearly everyone is starved for voltage when it is overloaded. At very least they all probably see a significant sag in voltage whenever someone's AC compressor starts or if anyone has other larger motors like the mentioned commercial air compressor.
I sincerely thank everyone for their knowledge and experience. We have 18 service connections over 2 transformers. From my house to first transformer pole #k11237is 111ft. Thats the 15kva. The other Pole / transformer w/ my cable co amp is Another 357ft south. Pole k3277