Have any of you installed the 4th generation Enphase Combiner 6C and Battery 10C equipment yet? I have been trying to get a definitive answer from Enphase but no luck yet. They describe several scenarios for achieving Rapid shutdown in the install guide, but they all include interrupting either the PV breakers in the combiner, or the PV aggregate breaker in conjunction with opening the RSD terminals on a header on the controller. If the combiner is installed indoors, all the breakers in the combiner are not accessible to emergency personnel outdoors. They describe disconnecting the internal conductors from the aggregate breaker lugs, extending them with an insulated splice/tap device, and routing them outside thru a safety switch and returning to the lugs, so that the outdoor switch is in series with the PV aggregate breaker, using a 3-pole switch, so that the 3rd pole can interrupt the RSD terminals as well when the switch is off. The page from the manual is attached. When I look at photos and videos of the unit it does not look like there is enough room to fit two polaris devices in the little cavity in order to extend those 4AWG conductors to an outdoor safety switch and back.
I have a project where it will be difficult to route the 4AWG power conductors for the 80A aggregate current outdoors, and in addition, the cost of a 3-pole 100A N3R switch is not low. I am having a hard time understnding why RSD cannot just be achieved by interrupting the RSD terminals (shown at location 5 in the diagram). From the description, it seems those terminals, when not shorted, will initiate rapid shutdown, and the support tech says that is the case, but then they say you still need to route the PVA aggregate conductors outside and interrupt those as well. I have not bee successful in speaking to anyone on the engineering team, they seem to want us to interface only with the tech support team. Routing 12 or 18AWG conductors outside from the RSD terminals to a small lockable toggle switch would be an inexpensive, easy solution, and it is how I have done it with SolarEdge and Sol-Ark before. Does anyone have any experience with this detail on that product?
I have a project where it will be difficult to route the 4AWG power conductors for the 80A aggregate current outdoors, and in addition, the cost of a 3-pole 100A N3R switch is not low. I am having a hard time understnding why RSD cannot just be achieved by interrupting the RSD terminals (shown at location 5 in the diagram). From the description, it seems those terminals, when not shorted, will initiate rapid shutdown, and the support tech says that is the case, but then they say you still need to route the PVA aggregate conductors outside and interrupt those as well. I have not bee successful in speaking to anyone on the engineering team, they seem to want us to interface only with the tech support team. Routing 12 or 18AWG conductors outside from the RSD terminals to a small lockable toggle switch would be an inexpensive, easy solution, and it is how I have done it with SolarEdge and Sol-Ark before. Does anyone have any experience with this detail on that product?