I'm looking at an Enphase system where the installer says that the output current to the MSP is limited to 50A by the Enphase PCS, which is also the max allowed on this panel. But they installed an 80A backfeed breaker since adding up the output currents of all of the microinverters and the battery and multiplying by 1.25 would require an 80A breaker.
They are claiming that the 80A breaker in a panel that will only allow 50A is just fine because they set the PCS at 50A.
I'm skeptical for two reasons, we have no clear way to determine if this setting is accurate and if it is limited to 50A why not install a 50A backfeed breaker?
Thoughs?
They are claiming that the 80A breaker in a panel that will only allow 50A is just fine because they set the PCS at 50A.
I'm skeptical for two reasons, we have no clear way to determine if this setting is accurate and if it is limited to 50A why not install a 50A backfeed breaker?
Thoughs?