fittowork1
Member
- Location
- hayward ca
- Occupation
- contractor
The lugs are single for 600 and the tenant mains are 100 amp ( I like 125 for the he'll of it but this is a system that was done before I started so somthings I can't change) by the way do you know if there is a min clearance for service conduits that run parallel to the ground.If its a Meter pack, what size lug kit is installed on the buss? or is there yet?
A meterpack generally defaults to a single 600 mcm lug per phase, or, you can get them with parallel lugs.
The lugs are interchangeable.
If the lugs are already installed on the meterpack, that would pretty much determine what size wire I'd feed it with.
What size are the tenant mains in the stack?
JAP>
Really appreciate the help