WOW if the non AFCI breakers are tripping then I'd say gremlins.
Try this:
There should be no current on the grounding wire. If this is a sub panel as it sounds like. Can you isolate the feeder grounding wire and place a amp probe around it. If you see current on the ground ( not the N) then trace it back from there. Turn on loads , Turn on oven.
And since when don't Siemens breakers trip to the center vs off. Maybe you have some counterfiet breakers.
Try this:
There should be no current on the grounding wire. If this is a sub panel as it sounds like. Can you isolate the feeder grounding wire and place a amp probe around it. If you see current on the ground ( not the N) then trace it back from there. Turn on loads , Turn on oven.
And since when don't Siemens breakers trip to the center vs off. Maybe you have some counterfiet breakers.