Entrance to and egress from working spaces

Status
Not open for further replies.

BJBoehm

Member
Referencing NEC 110.26 C and C3 and 110.33 A and A3. If there are two access doors (one double door for equipment and a single 36" door) are both doors or just the single door required to have panic bars? 110.26 C and 110.33 A 1 a is being met with regards to unobstructed to exit. Both doors have unobstructed means for exit. Question is: are panic bars on the single doors sufficient to meet code? or are both the single and double doors required to have panic bars.
Thanks for your input.
Bruce
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
What code cycle applies to this facility? If it is 2008, then I would say that only the single door needs the panic hardware, and then only if that door is within 25 feet of the working space.
 

BJBoehm

Member
Charlie,
Thanks for your post. It is 2008 code and yes, the door way is within 25' of the equipment. Appreciate your input.
Rgds.
Bruce
 