What constitutes Unobstructed Exit? I have a switchboard 25 feet long with front and back access only,and it is sitting in the middle of room with 42 inch clearance on both front and back sides.One end of the switchboard is against the side wall and has a 30 inch clearance on the other end.As allowed for unobstucted exit,one exit is planned on both front and back side of switchgear. Does the code define as to where along the length of the gear this exit has to be situated?If I look at Exhibit 110.17 of NEC handbook and situate the switchgear in the middle of room with required working space both in front and back of 480 Gear,my interpretation of 110.26C would be to have an exit door both in front and back, Please comment