jim k
- Northwestern Oregon
It seems to me that you'd want to bond the spa to the pond pump in this picture. However, as I read 680.40, as long as the pond pump is more than 5' away from the inner walls of the spa, there's no requirement for equipotential bonding between the two.
Nor can I find any requirement to bond the spa to the pond water. Were I not in Oregon, I might cite 680.26(B)(2), but the Oregon amended code has added a section at 680.42, which says, "Exception: The equipotential bonding requirements for perimeter surfaces in 680.26(B)(2) shall not apply to a listed self-contained spa or hot tub."
As far as I can see, there's a real danger of voltage potential between the spa water and the pond water. Am I missing a requirement?