Not sure if this helps, but I ran into a similar issue with data center in a hospital with an FM200 system... Here is what I came up with in regards to an EPO:
NFPA 75 deals with 'Protection of Information Technology Equipment'. Section 8.4.2.1 states "The power to all electronic equipment shall be disconnected upon activation of a gaseous agent total flooding system, unless the risk considerations outlined in Chapter 4 indicate the need for continuous power.'
Chapter 4, section 4.1 Risk Factors states "The following factors shall be considered where determining the need for protecting the environment, equipment, function, programming , records, and supplies:
1. Life safety aspects of the function (e.g. process controls, air traffic controls.)
2. Fire threat of the installation to occupants or exposed property
3. Economic loss from loss of function or loss of records
4. Economic loss from value of equipment"
Do you comply with any of the exemptions?
Tom