We have an IT room, all receptacles and UPS were fed out of a 208/120V panel with main shunt trip CB.
The CRAC unit serves the room is 480V/3PH, we have ran 480V circuit to a shunt trip - enclosed CB mounted in the room and feeds the CRAC unit.
Per, NEC we have to install an EPO at the room entrance, this EPO will shuts down power to both the panel and CRAC unit through shunt trip feature once EPO is activated by someone.
Question:
- Do we need to run 120V circuit to EPO to operate it or it can be operate at 24V DC? If it operates at 24V, should we need a step down xfmr to 24V or it comes as integral part of EPO?
- Do we tie fire alarm signal wiring to the EPO output too? (24V)
- What is the wiring connection between EPO and panel as well as between EPO and enclosed CB? Will this 120V or 24V or 277V?
* Note:
* The shunt trip coil for panel is 120V.
* The shunt trip coil for enclosed CB is 277V.