Where is it located in the code that a equipment grounding conductor has to be run with the feeder. A 3 phase system. 3h+1n+1g

Thanks
 

cpal

Senior Member
Location
MA
anothere reference might be 250.24 (5)
Generally speaking you never use a conductor that is intenionally grounded at the service equipment to normally non current carrying metal parts once you are down stream from the main.

It is permissable per 250.142 (restrictive language) but you need to read that section very carefully.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
NEC 250 Sec VI (250.110 + ) states what equipment must be grounded. 250.118 identifies "grounding conductors" which may also be your conduit and not necessarily a "seperate" conductor.
 