Equipment Grounding cond. insulation

Merry Christmas
Status
Not open for further replies.

MJReigle

Member
Here is my situation.....Installing new 4160 switch gear to feed multiple industrial motors. The engineer is specifying MV-105 cable to feed these motors(3-conductors + gnd.) My question is this...does the grounding conductor need to be MV-105 as well or can it be of a different insulation such as THHN?
 
The EGC may be bare or insulated (250.184(B)) for a solidly grounded neutral system. It is not required to be of the same insulation level as the phase cables.
 
MJReigle said:
Here is my situation.....Installing new 4160 switch gear to feed multiple industrial motors. The engineer is specifying MV-105 cable to feed these motors(3-conductors + gnd.) My question is this...does the grounding conductor need to be MV-105 as well or can it be of a different insulation such as THHN?
Depends on whether you are trying to comply with the NEC or with his specification. The NEC may not care (and I think it does not) but the engineer may care.
 
Thanks for the responses, the engineer specified it that way on his interpretation of the code. Now that I can convince him with an NEC reference I believe I can change his mind.
 