What do you think is the purpose of Equipment Grounding conductor EGC) for UNGROUNDED SYSTEM? Is it exactly the same as the solidy grounded system?
What do you mean by prevent arcing from induced voltage from lighting? Can you show us illustration please?No. It’s to prevent arcing from induced voltages from lightning. See 250.4
What does the EGC accomplish for preventing electric shock if it will not clear the fault?In an ungrounded system a line to ground fault won’t clear.
Do you mean that in ungrounded system you need two line to ground fault before it will trip the OCPD?When you get a second line to ground fault then you have a line to line short circuit, which is why GF detection is required
YesWhat does the EGC accomplish for preventing electric shock if it will not clear the fault?
Will it cause electric shock if there is no EGC in an UNGROUNDED SYSTEM?
Do you mean that in ungrounded system you need two line to ground fault before it will trip the OCPD?
On the first ground fault it will continue to function for UNGROUNDED SYSTEM?
What then does EGC accomplish in preventing shock or electrocution if it will not disconnect the OCPD in a single line to ground fault?Yes
Yes
Which is what I said
What hazard is created by a single line to ground fault on an ungrounded system?What then does EGC accomplish in preventing shock or electrocution if it will not disconnect the OCPD in a single line to ground fault?
Wil EGC have the same effect in High Resistance Grounded system?
What hazard is created by a single line to ground fault on an ungrounded system?
What does that have to do with Don's question?Section 250.24 (E)
1. To allow fault detectors to workWhat do you think is the purpose of Equipment Grounding conductor EGC) for UNGROUNDED SYSTEM?
I can later. Too many questions in a short time periodWhat do you mean by prevent arcing from induced voltage from lighting? Can you show us illustration please?
What does that have to do with Don's question?
The ungrounded system does not have bonding jumper, other than that is the same as a grounded systemIn an ungrounded system without a grounding conductor connected to the grounding electrode and connected to a metal enclosure of the service conductors you don't have a low impedance path to trip the breaker. In case of a phase to ground fault.
The ungrounded system does not have bonding jumper, other than that is the same as a grounded system
In an ungrounded system a line to ground fault won’t clear. When you get a second line to ground fault then you have a line to line short circuit, which is why GF detection is required