EQUIPMENT GROUNDING CONDUCTOR FOR UNGROUNDED SYSTEM

Status
Not open for further replies.

bobby ocampo

Senior Member
What do you think is the purpose of Equipment Grounding conductor EGC) for UNGROUNDED SYSTEM? Is it exactly the same as the solidy grounded system?
 

bobby ocampo

Senior Member
In an ungrounded system a line to ground fault won’t clear.
What does the EGC accomplish for preventing electric shock if it will not clear the fault?
Will it cause electric shock if there is no EGC in an UNGROUNDED SYSTEM?
When you get a second line to ground fault then you have a line to line short circuit, which is why GF detection is required
Do you mean that in ungrounded system you need two line to ground fault before it will trip the OCPD?

On the first ground fault it will continue to function for UNGROUNDED SYSTEM?
 

bobby ocampo

Senior Member
What happens to a person touching a metal part of the panel in an UNGROUNDED SYSTEM if one of the current carrying conductor touched the panel and there is no EQUIPMENT GROUNDING CONDUCTOR?
 

tom baker

First Chief Moderator
Staff member
What does the EGC accomplish for preventing electric shock if it will not clear the fault?
Will it cause electric shock if there is no EGC in an UNGROUNDED SYSTEM?

Do you mean that in ungrounded system you need two line to ground fault before it will trip the OCPD?

On the first ground fault it will continue to function for UNGROUNDED SYSTEM?
Yes
Yes
Which is what I said
 
What do you think is the purpose of Equipment Grounding conductor EGC) for UNGROUNDED SYSTEM?
1. To allow fault detectors to work
2. To allow 2nd faults to clear.
3. To bond all non-current caring metal parts together to reduce touch potential from things like capacitive effects.
4. To connect all non-current caring metal parts to Earth to provide equi-potential during normal operation.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
What does that have to do with Don's question?

In an ungrounded system without a grounding conductor connected to the grounding electrode and connected to a metal enclosure of the service conductors you don't have a low impedance path to trip the breaker. In case of a phase to ground fault.
 

tom baker

First Chief Moderator
Staff member
In an ungrounded system without a grounding conductor connected to the grounding electrode and connected to a metal enclosure of the service conductors you don't have a low impedance path to trip the breaker. In case of a phase to ground fault.
The ungrounded system does not have bonding jumper, other than that is the same as a grounded system
 

paulengr

Senior Member
In an ungrounded system a line to ground fault won’t clear. When you get a second line to ground fault then you have a line to line short circuit, which is why GF detection is required

Almost.

It’s line-ground-line. Usually the extra impedance won’t trip overcurrent protection.
 