Senior Member
- Location
- Indianola, Iowa
We have to increase the size of a circuit from a 60 amp circuit to an 80 amp circuit and have use of the existing 1" EMT for this new #4 THHN 3 phase and neutral circuit which has been engineered with a #4 equipment grounding conductor. Is it conceivable we could run the equipment grounding conductor on the outside of the 1" emt? The installation is through an office, drop ceiling and sheetrock wall. If we can we could use the exisiting conduit otherwise we have to upgrade to an 1 1/4".