Equipment grounding conductor size

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
So I have heat pump MCA 17.2A and MOCP of 25A.

Phase and neutral provided is sized per MCA #12 AWG.

Breaker provided is sized 25A per MOCP.

Question minimum equipment grounding conductor size should it be #12 AWG or #10 AWG?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Do you happen to look at a Code book ?

250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122,
but in no case shall they be required to be larger than the circuit conductors supplying the equipment
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122,
but in no case shall they be required to be larger than the circuit conductors supplying the equipment
'Ceptin' the parallel feeder installation. ;)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Even there they are not larger than the "circuit conductor", but they maybe larger than the ungrounded conductor in the individual raceways of the parallel system.
I agree, the ungrounded conductor size would be the sum of the conductors in parallel.
 