Re: equipment grounding conductor size
The big difference from '99 to '02 is that is the '99 code 250-122(b) only required an increase in the size of the EGC if the circuit conductors were increased to "compensate for voltage drop". In the '02 code any time the circuit conductors are larger than what is required by the ampacity tables for the size of OCPD, the EGC has to be increased proportionately to the increase in size of the circuit conductors. This change was made to close the "loophole" in the '99 code. If the inspector was told that the size increase was "just because that is the only size on the truck", he couldn't, under the '99 code, require an increase in size for the EGC. Now, under the '02 rules, any time the circuit conductors are larger than the minimum required size, the EGC must also be increased in size.