the 541 bolted fault amps would be a multiplyer of 3.6 for the Square D QOD breaker chart, this would give the 150 amp breaker a clearing time of 1.125 seconds to 30 seconds. The 5 second ICEA 150?C rating for #6 is 621.27 amps which means the insulation will be damaged in about 6 to 7 seconds at 541 amps, since it falls between the 1.125 to 30 seconds it looks like it can be damaged if I'm reading the QOD chart correctly, I can't belive it has that big of a window, but it seems to? I dont remember insta-trip breakers having this?
but a #4 looks like it would do just fine
If the voltage to X0 was 277 volts, the #6 would not be a problem, even at 240 volts.
Guys I'm learning too so go easy on me![]()
The problem comes with an arcing fault. When you have arcing fault, the magnitude of the fault is reduce significantly. With the arc impedance included, your 541 amps might be reduce to 300 amps or less. The time to trip the breaker might be in the minutes. This presents a hazard not only to the equipment but more importantly to humans working near the equipment.