What about these two examples with all 75 degree C terminations:
Ex. 1) 100 CB, w/ #3 THHN ungrounded conductors (100 amps), #8 EGC = OK
Ex. 2) 100 CB, w/ #2 THHN ungrounded in 52 deg C ambient (130 * .76 = 98.9 amps, next size up 100 amps), #8 EGC = OK
In the second scenario there is no increase in the ungrounded conductor size because a #3 THHN with that temperature correction would not be large enough in the first place. (110 * .76 = 83.6 amps)
Since the ungrounded conductor did not increase in size 250.122(B) would not apply.
Ex. 1) 100 CB, w/ #3 THHN ungrounded conductors (100 amps), #8 EGC = OK
Ex. 2) 100 CB, w/ #2 THHN ungrounded in 52 deg C ambient (130 * .76 = 98.9 amps, next size up 100 amps), #8 EGC = OK
In the second scenario there is no increase in the ungrounded conductor size because a #3 THHN with that temperature correction would not be large enough in the first place. (110 * .76 = 83.6 amps)
Since the ungrounded conductor did not increase in size 250.122(B) would not apply.