Equipment grounding conductor

Status
Not open for further replies.

jumper

Senior Member
This is an interesting question and I have changed my mind 3 times. I tend to feel that the egc cannot be paralleled unless each run is the same size as Table 250.122 states. No where does it state T. 250.122 or equivalent except in the case of cables-- 310.4(E) - 2008


seesaw.gif
 
Last edited:

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
This happens more and more I've noticed. The thread says there is an addition page (in this case page 3) but when I click on it, it brings me back to page 2. eh... what up with that? :?

It is a glitch that has been around for some time, even before the most recent format.

If you click on "Settings" (at the top any page) and scroll down to "General Settings" you can select a different number of posts per page other than the default of ten. I selected forty, which is the maximum, and have only had trouble once.

Another trick is to click "Post Reply" and you can see the all of the posts when you scroll down past the reply box.
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
It is a glitch that has been around for some time, even before the most recent format.

If you click on "Settings" (at the top any page) and scroll down to "General Settings" you can select a different number of posts per page other than the default of ten. I selected forty, which is the maximum, and have only had trouble once.

Another trick is to click "Post Reply" and you can see the all of the posts when you scroll down past the reply box.

Thanks for the tips.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
I am not ?in town? at the moment, and don?t have much time to participate in the forum. But I was asked (in a PM) to offer my opinion, so here it is.
(A) General. . . . conductors of size 1/0 AWG and larger comprising each
phase, polarity, neutral, or grounded circuit conductor shall be permitted to be connected in parallel (electrically joined at both ends).
I believe there are only seven kinds of conductors in the world, and they name four of them here (my emphasis above). I infer that the fifth, sixth, and seventh kinds (i.e., EGC, GEC, and bonding conductors) are not intended to be included in the list. If the rule was intended to cover all types of conductors, they would have either included all types, or they would not have explicitly named four of them. My conclusion: using two smaller wires in place of one larger wire is not an acceptable practice in the case of EGCs.

It may be all well and good to claim that anything not explicitly forbidden in the code is thereby allowed by the code, and that concept is indeed spoken of quite often and freely. But I don?t think there is any statement in the code that actually says that.


 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
It may be all well and good to claim that anything not explicitly forbidden in the code is thereby allowed by the code, and that concept is indeed spoken of quite often and freely. But I don?t think there is any statement in the code that actually says that.
Well, if it doesn't SAY that... ;^)
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
It may be all well and good to claim that anything not explicitly forbidden in the code is thereby allowed by the code, and that concept is indeed spoken of quite often and freely. But I don?t think there is any statement in the code that actually says that.

The code, by all intents and purposes, is the law. If it ain't illegal, it's technically legal. The code doesn't have to say it because it is basic facts.
To me the term "allowed by code" is just the default status if it isn't forbidden.
 

jumper

Senior Member
The code, by all intents and purposes, is the law. If it ain't illegal, it's technically legal. The code doesn't have to say it because it is basic facts.
To me the term "allowed by code" is just the default status if it isn't forbidden.

This is why the NEC gets so large and complicated. Every time someone comes up with a new way to do something dangerous, they gotta add another rule. :slaphead:
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
I am little confuse now, after looking at the link, in figure 6-9. I though paralled feed have to have same conductors size and length.
why it allow in figue 6-9. for each phase be diffferent ?
please help me clear up little.
thanks:?

the conductors of each phase etc have to be the same.

(B) Conductor Characteristics. The paralleled conductors
in each phase, polarity, neutral, grounded circuit conductor,
or equipment grounding conductor shall comply
with all of the following:
(1) Be the same length
(2) Have the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
 