Recently on a design build project, our electrical engineer has indicated we are to provide a properly sized equipment grounding conductors along with the secondary service lateral / feeders between the 3” ground bar located within the utility pad mount transformer, to the main switch gear.
We are also directed to eliminate the bond connection between the neutral and ground bar of the main switch gear, and provide all the grounding measures we typically would provide on a normal commercial project. These would include a NEC sized ground conductor to the main water line, building steel, and an external grounding triad.
In this particular case, it involves a 2000 Ampere, 120/208 VAC 3-Phase, 4-Wire underground service consisting of eight (8) sets of 4 pieces of 600 MCM Aluminum (AL) type XHHN, and a #4/0 AL ground in a 4" PVC Sch. 40.
I strongly disagree that the primary grounding of the service is derived by the bonding jumpers between the neutral terminal and grounding of the utilities pad mount transformer. Furthermore, I believe the "grounded" conductors or "neutral" conductor of the 3 phase / 4 wire system is all that is needed between the utility transformer and main distribution board. The bonding connection should be installed and adding equipment is nothing more than a redundant feature that is not required by the NEC.
I've installed hundreds of underground service laterals in over forty years in this trade and only seen this one other time. And on that occasion, the local utility indicated they did NOT want equipment grounds tied back to their ground bar.
Is this something new or have I been doing this wrong for all these years? I've never had a service fail an inspection so I'm wondering if the engineer is correct or crazy, if this is something new, or I just don't understand electricity anymore.....
Regards, David A.
Regards, David A.