wangyumei
- Omaha, Nebraska, US
I have a project with 175amp load at 240V, single phase. Due to the distances from the service transformer to the service panel, the feeder conductors are sized as 3 sets of (3-#4/0 AWG, plus ground). Per NEC section 250.122.B, the equipment grounding conductor in each set needs to be increased proportionnately per the phase conductors. So the grounding conductors will be #1/0. It is a pretty big grounding conductor. My question is that since this grounding increase is due to voltage drop, is there any exception in NEC for a smaller grounding conductor in this situation?