If you use the conduit system as your equipment grounding conductor, and have a wire ground installed as well, is the wire ground required to be sized per tabel 250.122?
Ok,
This is an existing installation and the #6 ground conductor is too small ( it should be a 1/0). Would the # 6 be required to be removed then?
I am inclined to agree, but it sure makes no sense.To be code compliant it would need to be removed or disconnected.
Chris
I am inclined to agree, but it sure makes no sense.
250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum
equipment grounding conductors of the wire type shall not be
smaller than shown in Table 250.122 ...
Think about a conduit that has both a 20A and a 15A branch circuit. If the electrician ran a #14 ground and a #12 ground he would be in violation, but would be Ok if he ran just a #12, or none at all if it was metal conduit.
Care to explain this?
Incidentally, it is pretty common for people to violate this rule.
Think about a conduit that has both a 20A and a 15A branch circuit. If the electrician ran a #14 ground and a #12 ground he would be in violation, but would be Ok if he ran just a #12, or none at all if it was metal conduit.
Could I have 2 TCs in a tray, one a 20A circuit with a #12 EGC and the other a 15A circuit with a #14 EGC inside the respective TC?
Think about a conduit that has both a 20A and a 15A branch circuit. If the electrician ran a #14 ground and a #12 ground he would be in violation, but would be Ok if he ran just a #12, or none at all if it was metal conduit.
Code reference please.
I like this question.
250.122 I think. It says what size EGCs have to be.
250.122(C) Multiple Circuits.
Where a single equipment grounding conductor is run with multiple circuits in the same raceway, cable, or cable tray, it shall be sized for the largest overcurrent device protecting conductors in the raceway, cable, or cable tray. Equipment grounding conductors installed in cable trays shall meet the minimum requirements of 392.3(B)(1)(c).
For multiple GEC's in a raceway I see no reason why you can't have a #14 for the 15 amp circuit and a #12 for the 20 amp circuit. They can even be spliced together at the junction box.