infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Sep 17, 2011 #21 chris kennedy said: No violation of 250.122(A) and (E)? Click to expand... (A) No (E) Flexible cords and fixture wires? (F) Parallel wouldn't apply since (F) applies to 310.10(H)
chris kennedy said: No violation of 250.122(A) and (E)? Click to expand... (A) No (E) Flexible cords and fixture wires? (F) Parallel wouldn't apply since (F) applies to 310.10(H)
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Sep 17, 2011 #22 infinity said: (E) Flexible cords and fixture wires? (F) Parallel wouldn't apply since (F) applies to 310.10(H) Click to expand... Sorry, I was looking at the 08. Nice clarification in the 11.
infinity said: (E) Flexible cords and fixture wires? (F) Parallel wouldn't apply since (F) applies to 310.10(H) Click to expand... Sorry, I was looking at the 08. Nice clarification in the 11.