- Windsor, CO NEC: 2017
- Hospital Master Electrician
Wrong. The answer is zero.bobby ocampo said:Depends on the measured resistance of the earth and prospective fault current.
tryinghard said:
peter d said:This is the finest Merry Go Round I have ever ridden.
George Stolz said:Wrong. The answer is zero.
bobby ocampo said:Sorry sir I don't understand what you mean please clarify.
Maybe you may answer directly the questions and comment point by point to the comments to prove your position.
The information that the illustration is based on comes right out of the IEEE green book. You can connect a ground rod to an ungrounded conductor and measure the voltage drop as you move away from the rod. I have done this experiment and gotten results that closely match the table in the Green Book. I also know that Mike has done this experiment an number of times at various locations. Your theory would be correct if the resistance of the earth was some what linear with distance from the rod, but it is very non-linear with a decrease in the resistance per unit of distance as you move away from the grounding electrode. This is often explained by the use of earth "shells" around the rod. The cross sectional area of each shell gets much larger as you move away from the rod and this results in a decrease in resistance.weressl said:These are the idiot diagrams I was refering to.
People who propagate such nonsense belong to the flat earth society. They need to think in complete circuits, but even that they are incapable to recognize.
They do NOT show the other grounding point at the transformer.
The voltage would be evenly divided between the grounded point at the source of the voltage driver and the fault location. so if the two locations are 20' apart then for each foot there would be aproximately 6V, but since the earth resistance varies as it is not a homogenous substance it would be more in someplaces and less in others.
But hey, it's on the Internet and is published by an "expert" so it must be true.
I couldnt agree more and I cant believe this has gone to this point. It is surreal the cheerleading for the conclusion to this point. Prove it is what I say and preach. Set up the real ife conditions the rescources are certainly here one less Rolex to help the little people live in safety. I have never seen a pole lighting circuit pulled without a grounding conductor in 35 years.weressl said:These are the idiot diagrams I was refering to.
weressl said:These are the idiot diagrams I was refering to...But hey, it's on the Internet and is published by an "expert" so it must be true.
tryinghard said:You guy's are talking about using earth as a fault path.
bobby ocampo said:If the system grounding in the illustration was an ungrouded system…
Step potential will be low enough that illustration will not happen but the metal pole may still be energized and the person touching the pole will receive an electric shock equal to 120 volts if the pole is not conneted to ground.
weressl said:A conductive path.
don_resqcapt19 said:The information that the illustration is based on comes right out of the IEEE green book. You can connect a ground rod to an ungrounded conductor and measure the voltage drop as you move away from the rod. I have done this experiment and gotten results that closely match the table in the Green Book. I also know that Mike has done this experiment an number of times at various locations. Your theory would be correct if the resistance of the earth was some what linear with distance from the rod, but it is very non-linear with a decrease in the resistance per unit of distance as you move away from the grounding electrode. This is often explained by the use of earth "shells" around the rod. The cross sectional area of each shell gets much larger as you move away from the rod and this results in a decrease in resistance.
Ouch teach em till it hurts!! Quote from the boss. I just did a 24 base parking lot with a groundrod 10'at every pole plus ground conductor #10 from bldg managers panel calculate this please. Real life.weressl said:IF that is the case, then it is only true to SINGLE ground rods and not industrial or commercial use structures where
If the above is true then the Code is negligent in addressing other than single family dwelling installations.
- muiltipoint grounding rods exist with interconnecting grounding cables between them
- steel structures in industrial plants where the 'ground' is steel decking or grating.
The 'shells' exist, however they are immaterial since there is only a linear path exist between the ground rod and the knee of the poor fella...
bobby ocampo said:?Connection to earth is used to reduce the potential of the energized metal piece to earth potential. This is also the purpose of connecting the neutral of the solidly grounded system so that potential of the current carrying conductor will be limited to line to ground fault.
bobby ocampo said:Connection to earth is used to reduce the potential of the energized metal piece to earth potential. This is also the purpose of connecting the neutral of the solidly grounded system so that potential of the current carrying conductor will be limited to line to ground fault.
bobby ocampo said:Based on the illustration, what will happen if another grounding rod is installed 3 feet and 5 feet respectively and is bonded to the ground rod installed near the post with zero potential?
bobby ocampo said:What is the assumed resistance of the earth in this illustration?
bobby ocampo said:To reduce step potential to ground or earth as in this illustration there are two solution. One is when fault current is low and another is when resistance is low...
If resistance to ground is reduced to a small amout because of installation of another grounding rod bonded to the first grounding rod, step potential will be reduced.
It is in the OHMS law section of the NEC. Have you ever heard of this section??tryinghard said:Where are you getting this in the NEC?
Which is why a GFCI would be worthless on an ungrounded system.tryinghard said:Why would electrocution happen with an ungrounded system? Do you understand there is no phase connection to earth at all in an ungrounded system? There will not be potential to ground earth.