graino
- Plainfield Illinois USA
I've been wresting with the equipment grounding conductor requirements listed in 250.110, 1 through 6. Specifically in an older home with two wire non-metallic sheathed cable minus any equipment grounding conductors. It appears as though an ungrounded two prong receptacle can be "legally" replaced with a GFCI receptacle for connecting cord and plug connected equipment requiring an EGC? Is this correct? If so what code article allows this? Secondly what about fixed in place equipment requiring an ECG when none are available? Let's take a specific example like a ceiling fan requiring an EGC. If none are available is an EGC still required? Must an EGC be routed to the equipment or is something like a Ground Fault Breaker a code compliant alternative? If so where is it allowed in the NEC?
Thanks for any insights you can provide on this topic.