TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
The situation I am looking at is in the natural gas industry, Class I, Div 1, Group D. In NEC 202, Article 501.10(A) (1) it lists the permitted wiring methods. Types of both armored and non-armored cable is permitted. Let's say I am wiring from a controller to a pressure transmitter fitted to gas piping. If I use armored cable, the armor satisfies the equipment grounding requirement. If I use non-armored cable another means of equipment grounding is required. Since this is gas piping I may not use the piping as an equipment ground. If I use a conductor within the cable, it must be at least 14 ga (not likely in instrument cable.) If I use a conductor outside the cable it must be at least 6 ga and attached to a fitting with a grounding screw?
It seems for gas piping, you need to choose armored cable in order to provide an equipment ground. Or am I missing something?
It seems for gas piping, you need to choose armored cable in order to provide an equipment ground. Or am I missing something?