Were there wire type egc's in that panel?. It's not unheard of to not have any wire egc's nor a ground bar if it's all metal conduit and the conduot system is the egc
Yep, works fine until someone runs say a piece of MC cable to the panel and instead of adding a ground bus sticks the EGC into the neutral bus. See that a lot.
So the incoming EGC was just landed to the enclosure?... 240v 3 phase 4 wire panel . And noticed that there was no grounding bar ...
Yellow all I have a question about grounding .the other day I ran wire to a 240v 3 phase 4 wire panel . And noticed that there was no grounding bar . Just the neutral bar . Should there not be a grounding bar for equipment grounding
Yep, works fine until someone runs say a piece of MC cable to the panel and instead of adding a ground bus sticks the EGC into the neutral bus. See that a lot.
Were there wire type egc's in that panel?. It's not unheard of to not have any wire egc's nor a ground bar if it's all metal conduit and the conduot system is the egc
(4) An equipment grounding conductor that is part of
another branch circuit that originates from the enclosure
where the branch circuit for the receptacle or branch
circuit originates
Yes the electrical sys is all metal conduit.
crosspost.....
so , would installing a 'snap around' grounding bushing on said emt, and making it to a Gbar then be complaint to land any ecg's introduced?
~RJ~
...Just screw the ground bar to the enclosure.
Not a problem if the panel is the main service & the neutral is bonded to the can.
Thank you all for your reply. The system is metallic conduit
And not a service panel . And noticed that the nutreal bar is
Bonded to the panel ,which if I understand artical 200,250 is a no,no .