The same person that has to verify that a single ground rod has 25 ohms or less resistance to ground.Originally posted by mpd:
iwire if the NEC had a definition like what you are saying, who would certify that EGC system
The temperature limit of a bare EGC is the same as that of the insulated circuit conductors so that the hot EGC does not damage the grounded ungrounded conductors.As an EGC can be bare to concern one self with overheated EGC insulation seem fruitless.
If the EGC is melted by the fault current, or even it it gets hot enough to damage the insultation on the other conductors there is a violation of 250.4(A)(5).(5) Effective Ground-Fault Current Path Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a permanent, low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be considered as an effective ground-fault current path.
I don't doubt it and it is probably here as well.Originally posted by don_resqcapt19: