Equipment space

Status
Not open for further replies.

nickelec

Senior Member
Location
US
I have to upgrade this panel and service I'm 100%certin that steam line is in the dedicated space and I need to move the panel anyone disagree
61a3e7df2ae2dc185c0d52ecd2604107.jpg


Sent from my SM-G950U using Tapatalk
 
If I installed the new panel under the steam line would it still be considered inside the space

Sent from my SM-G950U using Tapatalk
 
I have to upgrade this panel and service I'm 100%certin that steam line is in the dedicated space and I need to move the panel anyone disagree

Sent from my SM-G950U using Tapatalk

It doesn't seem to be in the dedicated space, but does appear to be in the working space.
 
So if that steamline were 6 foot 7inches off the floor and the panel is mounted underneath it then I would be in the clear correct

Sent from my SM-G950U using Tapatalk
 
Cabinetis coming down when u replace the panel im worried about the steam line

Sent from my SM-G950U using Tapatalk
 
So if that steamline were 6 foot 7inches off the floor and the panel is mounted underneath it then I would be in the clear correct

Sent from my SM-G950U using Tapatalk

110.26(E)-Dedicate equipment space is the space above the panel, the width and depth of the panel and up to 6 feet above the panel or to the structural ceiling (whichever is lower), and cannot anything other than that which is dedicated to the electrical installation (cables, raceways, etc.).

110.26(A)(1) through (3)- Clear working space is the space in front of the panel, 30 inches wide by 36 inches deep and 6.5 feet high, and this space cannot contain anything else.

If the steam pipe is in either of the above spaces, it would be a violation.
 
My review of the photo tells me that the steam line is not directly over the panel. So you would not have a problem with dedicated space. It then would come down to whether the steam line is at least 6.5 feet above the floor.
 
110.26(E)-Dedicate equipment space is the space above the panel, the width and depth of the panel and up to 6 feet above the panel or to the structural ceiling (whichever is lower), and cannot anything other than that which is dedicated to the electrical installation (cables, raceways, etc.).

110.26(A)(1) through (3)- Clear working space is the space in front of the panel, 30 inches wide by 36 inches deep and 6.5 feet high, and this space cannot contain anything else.

If the steam pipe is in either of the above spaces, it would be a violation.

How does dedicated space apply to panelboards recessed in wood framing? Are cross-members of the wood framing and thermal insulation allowed within it?
 
How does dedicated space apply to panelboards recessed in wood framing? Are cross-members of the wood framing and thermal insulation allowed within it?
The code does not explicitly address this situation. One could take the view that all that stuff is "foreign" to the electrical installation, and throw a flag on that play. My view is that this is not a code violation. I would not call a wood framing member "equipment." Also, such an installation does provide protection for the panel, as is required by 110.26(E). Finally (and I have no code wording to back this up), I believe the purpose of this article is to allow for future installation of additional conduits. That, I believe, is why it only applies to four specific components, and not (for example) to transformers, disconnect switches, or VFDs. A flush mounted panel is not going to be getting any new conduits, or at least not without a great deal of difficulty. That is why most plans and specs require spare conduits to be run from a flush mounted panel to a space above the suspended ceiling - for future circuits.

 