the termination temperature limitation determination pads any continuous load current by 25% for minimum conductor sizing. For minimum conductor ampacity, the continuous load current is not padded.
Necro'ing an older thread. What do you mean by this? I thought that conductor ampacity should be sized for 125% of the continuous load as per 210.19(A)(1)(a) and 215.2(A)(1)(a).
I'm still unclear why temperature adjustment factors do
not apply to terminations. It would make sense to me in event that the terminations are made inside of a building where the climate is maintained to 26-30C. Otherwise, what makes the terminations special such that ambient temperature won't affect their performance/integrity? Is it because the ambient temperature adjustment is mainly to protect the insulation, of which a termination has none?
For example, below is a practice test problem that I'm pondering. Why would we not apply temperature correction to the #10 AWG termination rated for 60°C, making the effective ampacity of the termination equal to 30A x 0.82 = 24.6 amps? Surely the equipment to which the termination is mated could be outdoors in this 50°C environment.
.
.
A branch circuit is designed using 10 AWG THHN 90°C copper conductors. The ambient temperature is 50°C for a desert installation. The circuit uses a switch whose terminals are rated for 75°C and a circuit breaker whose terminals are rated for 60°C. What is the maximum permitted ampacity of the circuit?
These are several issues in this problem. The first is the basic ampacity of the conductors. This is given by Table 310.15(B)(16) on Page 161 as 40 Amps. The temperature deration for 50°C is 0.82. (40A) x (0.82) = 32.8 Amps. This is the ampacity of the actual conductors. Now, we must look to see how much current the terminations can handle. One end is listed for 75°C but the other end is only listed for 60°C. Therefore, we must go with the smaller per Article 110.14(C) on Page 38. Per Article 110.14(C)(1), for 60°C, the maximum permitted ampacity is 30 Amps. So, although the conductor itself is good for 32.8 Amps, the ends are only good for 30 Amps. (Actually, one end is good for 30 Amps and the other is good for 35 Amps). In any event, the weakest link in the chain is 30A.
(C) 30A