Is it necessary to have an equipotential bonding grid under a wooden deck for an outdoor spa? And how to do that after the deck has been built?
technicaly, yes. Realistically, ???????????????????????Is it necessary to have an equipotential bonding grid under a wooden deck for an outdoor spa? And how to do that after the deck has been built?
According to the powers that be in my state you need the bonding grid even when your elevated a floor or more above grade.
I'd say no e-bonding grid/perimeter surface grid required. How do you connect to a wood deck?
I'd say no e-bonding grid/perimeter surface grid required. How do you connect to a wood deck?
what i would do then is to install it around the slab 3ft all the way around , if inspector don't like that then i guess you tear the slab out an start new.
Do you think a wood deck is an "unpaved surface"?
I have to say the bonding grid under a deck is seems useless but it is in the NEC.
I have a related question. Outdoor spas shall comply with the provisions of Parts I and II of article 680. So what about 680.26(C)? The interior of spas are non-metallic, are you now required to drop a piece of metal in the water in order to have the necessary surface of 9 sq inches of conductive metal in contact with water?
Is it a surface?
Is it paved?
Staple the grid the bottom of the deck.![]()