Discussed during the 2005 cycle but not clearly addressed were pools that were unpaved within the 3 ft area around the edge of the pool. As the shock hazard potential exists with unpaved earth as well as concrete or various types of pavers, this section was expanded to clearly address bonding to all types of perimeter constructions. Proposed 680.26(B)(2)(b) text is a new bonding option. Due to the limited width of the perimeter surface, a single 8 AWG solid copper conductor should be sufficient to collect any ground currents circulating through the pool perimeter.